1. Glazing in swinging doors except jalousies.
2. Glazing in fixed and sliding panels of sliding door assemblies, and panels
in sliding and bifold closet door assemblies.
3. Glazing in storm doors.
4. Glazing in all unframed swinging doors.
5. Glazing in doors and enclosures for hot tubs, whirlpools, saunas, steam rooms, bathtubs, and showers. Glazing in any part of a building wall enclosing these compartments where the bottom exposed edge of the glazing is less than 60 inches (1524 mm) measured vertically above any standing or walking surface.
6. Glazing in an individual fixed or operable panel adjacent to a door where the nearest vertical edge is within a 24-inch (610 mm) arc of the door in a closed position and whose bottom edge is less than 60 inches (1524 mm) above the floor or walking surface.
7. Glazing in an individual fixed or operable panel, other than those locations described in Items 5 and 6 above, that meets all of the following conditions:
7.1. Exposed area of an individual pane larger than 9 square feet (0.836 mm).
7.2. Bottom edge less than 18 inches (457 mm) above the floor.
7.3. Top edge more than 36 inches (914 mm) above the floor.
7.4. One or more walking surfaces within 36 inches (914 mm) horizontally of the glazing.
8. All glazing in railings regardless of an area or height above a walking surface. Included are structural baluster panels and nonstructural infill panels.
9. Glazing in walls and fences enclosing indoor and outdoor swimming pools, hot tubs, and spas where the bottom edge of the glazing is less than 60 inches (1524 mm) above a walking surface and within 60 inches (1524 mm) horizontally of the water’s edge. This shall apply to single glazing and all panes in multiple glazing.
10. Glazing adjacent to stairways, landings and ramps within 36 inches (914 mm) horizontally of a walking surface when the exposed surface of the glass is less than 60 inches (1524 mm) above the plane of the adjacent walking surface.
11. Glazing adjacent to stairways within 60 inches (1524 mm) horizontally of the bottom tread of a stairway in any direction when the exposed surface of the glass is less than 60 inches (1524 mm) above the nose of the tread.
Exception: The following products, materials and uses are exempt from the above hazardous locations:
1. Openings in doors through which a 3-inch (76 mm) sphere is unable to pass.
2. Glazing in Section R308.4, Items 1, 6, or 7, in decorative glass.
3. Glazing in Section R308.4, Item 6, when there is an intervening wall or other permanent barrier between the door and the glazing.
4. Glazing in Section R308.4, Item 6, in walls perpendicular to the plane of the door in a closed position, other than the wall toward which the door swings when opened, or where access through the door is to a closet or storage area 3 feet (914 mm) or less in depth. Glazing in these applications shall comply with Section R308.4, Item 7.
5. Glazing in Section R308.4, Items 7 and 10, when a protective bar is installed on the accessible side(s) of the glazing 36 inches ± 2 inches (914 mm ± 51 mm) above the floor. The bar shall be capable of withstanding a horizontal load of 50 pounds per linear foot (730 N/m) without contacting the glass and be a minimum of 1-1/2 inches (38 mm) in height.
6. Outboard panes in insulating glass units and other multiple glazed panels in Section R308.4, Item 7, when the bottom edge of the glass is 25 feet (7620 mm or more above grade, a roof, walking surfaces, or other horizontal [within 45 degrees (0.79 rad) of horizontal] surface adjacent to the glass exterior.
7. Louvered windows and jalousies complying with the requirements of Section R308.2.
8. Mirrors and other glass panels mounted or hung on a surface that provides a continuous backing support.
9. Safety glazing in Section R308.4, Items 10 and 11, is not required where:
9.1. The side of a stairway, landing or ramp has a guardrail or handrail, including balusters or in-fill panels, complying with the provisions of the handrail and guardrail requirements; and
9.2. The plane of the glass is more than 18 inches (457 mm) from the railing; or
9.3. When a solid wall or panel extends from the plane of the adjacent walking surface to 34 inches (86 mm) to 36 inches (914 mm) above the floor and the construction at the top of that wall or panel is capable of withstanding the same horizontal load as the protective bar.
10. Glass block panels complying with Section R610.How do you identify safety glass?
Country-specific laws similarly require a permanent label on most or all safety glass. In the UK, for instance, tempered glass must include a “T,” and laminated glass must include an “L.” New Zealand requires, according to Clause 303.7 of NZS 4223:Part3:1999, that all safety glass include a label at the bottom that includes the following information:R308.1.1 Identification of multipane assemblies. Multipane assemblies having individual panes not exceeding 1 square foot (0.09 m2) in exposed area shall have at least one pane in the assembly identified in accordance with Section R308.1. All other panes in the assembly shall be labeled "16CFR1201."
Section R308.1 details identification as follows:
R308.1 Identification. Except as indicated in Section R308.1.1, each pane of glazing installed in hazardous locations as defined in Section R308.4 shall be provided with a manufacturer's or installer’s label, designating the type and thickness of glass and the safety glazing standard with which it complies, which is visible in the final installation. The label shall be acid-etched, sandblasted, ceramic-fired, embossed-mark, or shall be of a type which, once applied, cannot be removed without being destroyed.
(a) the name, registered trademark or code of the manufacturer or supplier;(b) the type of safety glazing material. This may be in the form of a code, such as T for Toughened glass, or L for Laminated Glass, as indicated by the relevant test Standard (refer AS/NZS 2208);(c) the Standard to which the safety glazing material has been tested, e.g. AS/NZS 2208;(d) if applicable, the classification relating to impact test behaviour, i.e., A for Grade A, B for Grade B, C for Grade C.