How to Inspect and Correct a Vented Crawlspace
by Nick Gromicko, CMI® and Ben Gromicko
This article explains the issues and concerns with conventional ventilated crawlspaces and outlines prescriptive measures for improvements that will create healthier and more durable spaces. This information is provided by the U.S. Department of Energy Building Technologies Office Building America Program "Guide to Closing and Conditioning Ventilated Crawlspaces."
Home inspectors should use this how-to guide as a tool to help them perform inspections of crawlspaces, identify indications of defects associated with crawlspaces, and properly recommend strategies to convert a traditional crawlspace with open foundation vents, and poor design and construction into an unvented, insulated, and conditioned space.
This article is intended to apply to crawlspace foundations that are constructed of solid concrete or concrete masonry units (CMUs) with a continuous brick cap or bond beam that minimizes the potential for moisture movement from the ground through the masonry cores toward the wood floor structure (see Figure 1).
Figure 1. Types of crawlspace foundation systems applicable to this article.
The methods described here are not the only acceptable ways to treat a crawlspace but represent a proven strategy that works in many areas of the United States. The designs discussed here may or may not meet the local building codes.
Crawlspaces in the United States typically are constructed of hollow masonry block or poured concrete stem walls. In general, these foundations are equipped with permanent vents to the outdoors that are intended to furnish cross-ventilation to prevent moisture in the space. Until recently, houses built over vented crawlspaces have been constructed with little or no regard to moisture-causing sources that can contribute to long-term structural damage and pose health hazards. The interior and exterior detailing of many construction components needs to be evaluated and installed correctly to combat unwanted moisture within a crawlspace. Past research has shown that a conventionally vented crawlspace that has been converted into an unvented and conditioned space tends to operate similarly to houses with basements, with several benefits for the homeowner (BSC 2004), including:
  • energy savings;
  • increased comfort;
  • moisture control;
  • long-term durability; and
  • healthier air quality.
Research has shown that vented crawlspaces located in mixed or hot-humid climates tend to increase the moisture level within the space instead of keeping it drier. This increased moisture then condenses on the colder wood surfaces of the floor framing, promoting fungal growth and wood damage. Vented crawlspaces also have the potential to rob energy savings from the living spaces of the home if the appropriate insulation strategy has not been followed correctly. Retrofitting a vented crawlspace into an unvented, insulated, sealed and dry space requires more than just sealing off the vent openings. Not considering other details within the crawlspace and simply sealing the vents could make the situation worse, increasing the levels of moisture and potentially creating a deadly situation if naturally ventilated types of combustion equipment are located in the crawlspace. Depending on the conditions, it might be best to implement the closed-crawlspace strategy slowly to minimize the effects of materials rapidly drying out. Rapid and excessive drying can potentially cause cosmetic damage to wood-based finish products in the living area of the home. Conversely, swollen and cupped hardwood flooring may flatten during the drying process.
With regard to the use of rigid foam boards as the insulation strategy for walls and band joist areas, Advanced Energy (2005) says:
  • Foam plastic insulation receives special scrutiny in residential building codes because some foam insulations have the potential to release toxic or flammable gases when heated, or they can accelerate the spread of fire if they ignite. To reduce these risks, most codes require a thermal barrier (typically, ½-inch gypsum board or equivalent) or an ignition barrier (typically, ⅜-inch gypsum board or equivalent) over foam insulation. However, several foam insulation products have been designed and tested to reduce or eliminate those risks. Duct products can be installed without a thermal barrier or ignition barrier with the appropriate documentation.
  • Houses located in flood zones may be required to have flood vents. Flood vents are openings in a foundation wall that automatically allow the free passage of flood water into and out of a foundation to equalize hydrostatic forces on the foundation walls. When required in a closed crawlspace, the homeowner should choose a flood vent model that reduces standby air leakage as much as possible. The Federal Emergency Management Agency and the National Flood Insurance Program specify the design requirements for flood vents, as well as the guidelines for where they must be implemented. The 2000 (and later) International Codes meet these requirements. To determine if a property is located in a Special Flood Hazard Area that would require flood vent installation, contact your local building inspections department or governing authority.
Basic Concepts: Moisture Transport
Where Does the Moisture in a Crawlspace Come From?
There are four primary modes of moisture migration into a home: capillary action; bulk moisture transport; air transport; and vapor diffusion. Each of these modes, described in the following list, must be controlled to preserve comfort, health, and building durability.
Capillary action (see Figure 2):
  • Water wicks through porous materials or through small cracks.
  • Primary sources are rain and groundwater.
 Figure 2. Capillary action
Bulk moisture transport (see Figure 3):
  • Moisture flows through holes, cracks and gaps.
 Figure 3. Bulk moisture transport
Air transport (see Figure 4):
  • Unsealed penetrations and joints between conditioned and unconditioned areas allow air containing water vapor to flow into enclosed areas.
  • The primary sources are water vapor in the air and soil gas.
 Figure 4. Air transport
Vapor diffusion (see Figure 5):
  • Water vapor in the air moves through permeable materials.
 Figure 5. Vapor diffusion
Evaluation
The first step in developing a plan for a crawlspace conversion is to perform a thorough inspection of both the exterior and interior conditions. The following areas and specific details must be attended to before starting the sealing and insulating of any crawlspace:
  • Immediate health and safety issues:
    • electrical system;
    • mechanical systems (for the threat of carbon monoxide);
    • framing (for potential mold growth);
    • hazardous materials storage (including the presence of asbestos); and
    • radon.
  • Exterior moisture sources:
    • roof drainage away from the house;
    • grading around the house;
    • lawn sprinklers;
    • foundation waterproofing and drainage; and
    • access door.
  • Interior moisture sources:
    • leaking drains or supply plumbing;
    • condensate drain;
    • standing water on the floor;
    • crawlspace floor;
    • vent openings;
    • sump pump crock pit; and
    • water softener discharge.
  • Other contaminants and issues:
    • feces, carcasses, and other animal waste
    • animal infestation
    • termites and carpenter ants
    • thermal breaks;
    • insulation strategy; and
    • space conditioning.
Immediate Health and Safety Issues
Electrical Inspection
Assessing the current electrical system within the crawlspace is one of the first steps to take. A qualified electrician might need to be consulted if there is exposed or damaged wiring within the crawlspace. If there is a risk of shock or electrocution from faulty wiring, postpone the inspection of the interior systems until any issues have been resolved and the space is safe.
Mechanical Systems/Carbon Monoxide
Establish the type of space conditioning equipment and water heaters. If fuel-fired combustion appliances are located in the crawlspace, it is important to determine their venting and combustion air sources. These life-safety strategies are a critical first step in the overall renovation efforts of the crawlspace. If natural draft-vented appliances that depend on combustion air from the open vents in the foundation are present, equipment upgrades and replacement or alterations to the makeup air methods will be necessary. The best strategy is to replace natural draft-vented appliances with sealed combustion, direct-vent furnaces or all-electric heat pumps. The direct-vent gas furnaces draw combustion air directly from outside through piping to the unit. All combustion byproducts are vented through sealed piping to the outdoors, minimizing the possibility of any carbon monoxide spillage. Verify that an operational carbon monoxide detector is installed in the crawlspace.
If there are any gas line regulators within the crawlspace, they will need to be moved so they vent to the outdoors.
Mold/Framing
Finding some traces of mold or mildew is common in a poorly detailed and ventilated crawlspace. The floor deck and all framing in the crawlspace are vulnerable to some level of fungal attack if moisture levels within the crawlspace go unchecked. Once high levels of moisture are present, moisture will tend to condense on the cooler surfaces of the wood framing and floor deck. These areas are easy to observe and are an indicator of high moisture content. Any surface mold or fungal growth will require a certified mold inspector to conduct an inspection and determine an appropriate remediation protocol to clean all the components before work can proceed. Structural repairs to framing components might be necessary if there is extensive damage or wood rot.
Asbestos
Exposure to asbestos increases a person’s risk of developing lung disease. Old crawlspaces might have asbestos-based insulation wraps on ductwork and plumbing pipes. If asbestos is discovered, a certified asbestos abatement firm will have to be contracted to inspect and determine the best treatment strategy for the particular situation. General movement and unintentional contact with asbestos-based products can stir the fibers, which can then become airborne within the confined space, posing a health risk to anyone in the immediate vicinity.
 Hazardous Materials Storage
If any hazardous materials have been stored in the crawlspace (e.g., creosote-treated lumber, pesticides, etc.), they must be completely removed and properly disposed of.
Radon
In areas where radon is a risk or where the local residential code requires control of radon or other soil gases, houses with closed crawlspace foundations must be tested and monitored by a certified radon tester. If necessary, an approved mitigation system must be installed. The U.S. Environmental Protection Agency (EPA) and the U.S. Surgeon General recommend testing all homes for radon.
Installing a passive radon mitigation system before undertaking all sealing work could be necessary in radon-prone areas. After the crawlspace is closed and sealed, final testing for radon should be conducted. Converting the passive system to an active system is easily accomplished if readings exceed the EPA’s acceptable levels.
 Exterior Moisture Sources
 Roof Drainage Away from the House
Inspect the roof’s bulk water discharge strategy, including all gutters and downspouts, to ensure bulk water runoff is not allowed to collect next to or near the foundation. Downspouts should discharge into drains that are directed to a storm sewer system, retention pond, daylighting (if the land topography permits), or yard bubblers that are a minimum of 10 feet away from the foundation.
 Grading Around the House
Evaluate the grading at the perimeter of the house. Ideally, the ground should slope a minimum of 5% away from the foundation walls for at least the first 10 feet in order to direct groundwater away from the structure. If the slope cannot be established because of the home’s elevation and surrounding grade, a surface drainage system should be installed. This type of system collects water and diverts it away from the foundation.
Before any excavation work starts, the homeowner should identify any underground utilities that enter the house and notify the respective utility companies, as required.
Lawn Sprinklers
Turn on all sprinklers installed near the foundation to observe their flow pattern. The sprinklers must be positioned so that they don't subject the foundation or the immediate vicinity to water.
Foundation Waterproofing and Drainage
Implementing foundation waterproofing and a perimeter drain strategy on the exterior walls will be required on exceptionally problematic sites. Such sites typically have high groundwater or water flow against the foundation that cannot be remediated in any other way.
Foundation Vents
The foundation vents can be another source of bulk water entry. Make sure that they are not too low in relation to the exterior grade. If the vents fall near or below grade, they will need to be filled in with block, brick or concrete and sealed to prevent water entry.
 Access Door
Inspect the general location and overall weather seal of the access door. The access door should be located high enough off of grade to prevent groundwater runoff and snowmelt from entering the crawlspace. If the door is located too low and there is not enough clearance to adjust the entry height, remove the door, seal the opening, and install a new entry at a different location at the exterior that will accommodate the clearance. If no suitable location meets these criteria, cutting an access way through the floor system within the house will be required.
 Interior Moisture Sources
 Standing Water on the Floor
Any standing water must be eliminated, and the source of the water identified and repaired to prevent a recurrence that would raise the moisture levels within the space. Standing water typically indicates a leaking pipe from above or groundwater entering the space from outside the building or under the floor.
Leaking Drains or Supply Plumbing
Conduct a thorough inspection of all drains and supply plumbing located within the crawlspace to make sure that no leaks are adding moisture to the space.
 Mechanical System Condensate Drain
Evaluate the entire length of the condensate drain, from the air handler to the discharge point. Because of the potentially corrosive discharge from sealed combustion furnaces and air conditioners, condensate drains must be installed as required by local jurisdictions. They must be properly supported and routed directly to a sealed sump crock lid, a floor drain fitting, or a sanitary sewer.
In addition to the primary drain (and as a safety precaution if the primary drain fails), an auxiliary drain pan with a separate drain beneath any cooling or evaporator coil is recommended to prevent condensate from flooding the crawlspace. Inspect the current condition of the crawlspace floor because it is a critical factor in directing any surface water toward collector drains and the sump. It also minimizes moisture movement from the soil into the crawlspace environment. Poor sealing practices of the polyethylene vapor barrier allow ground moisture to infiltrate through gaps or open seams in the barrier, increasing the relative humidity of the crawlspace. Grading the base to a minimum 3% slope toward low-spot collector drains that can move water directly to the sump is necessary to eliminate ground moisture from seeping into the space.
Vent Openings
All intentional, operable or fixed foundation vents will need to be sealed to prevent warm moisture-laden air from being drawn into the crawlspace. If the vents are too low and appear likely to permit bulk water intrusion into the crawlspace, they will need to be sealed with concrete block, brick, concrete, or glass block windows to prevent water entry.
Sump Pump
Inspect all sump pump crock pits installed in the crawlspace, looking at the detailing of their lids and any drainpipe penetrations. Missing lids and an absence of sealing will allow moisture to enter and increase the relative humidity of the crawlspace.
The 2015 IRC, Chapter 4, Section R405.2.3, Drainage System, states the following:
  •  In other than Group I soils, a sump shall be provided to drain the porous layer and footings. The sump shall be at least 24 inches in diameter or 20 inches square, shall extend at least 24 inches below the bottom of the basement floor, and shall be capable of positive gravity or mechanical drainage to remove any accumulated water. The drainage system should discharge into an approved sewer system or to daylight.
In areas with high water tables, installing a battery backup system to the pump is recommended to aid in drainage during power outages.
Drainpipes
To prevent any water backups through drainpipes, consider the following recommendations
(from Advanced Energy 2012, p. 12):
Use a backflow valve in crawlspace drains and a check valve in sump pump out-flow pipes to prevent reverse flow of outside water into the crawlspace and to reduce the chance of vermin entry. Floor drains with P-traps that connect to the whole-house plumbing waste drain or to a municipal sewer system may allow entry or sewer gases if or when the trap dries out and pose a risk of sewage backup.
Other Contaminants
 Feces, Carcasses, and Other Animal Waste
Old existing crawlspaces, if left unattended, can contain large amounts of animal droppings or carcasses of animals that have found a way into the crawlspace and died. Be prepared for this possibility.  If these contaminants are found, a thorough cleanup must be conducted before proceeding.
Animal Infestation
In some cases, crawlspaces that have been left unattended or neglected can harbor wild animals. Recognizing the exterior details that allow entry and exit and other activity will help prepare the inspector. Depending on the severity, the local animal control agency might need to assist in removing any unwanted animals.
Pest Control
Termites and carpenter ants are known to thrive in dark, damp places that have a readily available food source nearby. Inspecting the foundation walls and framing for signs of wood-destroying organisms is required before proceeding. Any observed indications of infestation will then require a more in-depth inspection and treatment by a pest control professional.
 Thermal Issues
 Insulation Strategy
The current insulation levels, location and integrity will need to be assessed to determine the appropriate strategy for the climatic region. Any existing fiberglass batt insulation in the floor system or draped over the foundation walls should be removed and discarded. A good work plan will include a thorough specification and implementation strategy for thermal insulation.
 Space Conditioning
Crawlspaces must always have a drying mechanism. One of the most effective ways is to condition the crawlspace is by bringing in a reduced amount of conditioned air from the mechanical system to temper the space as if it were part of the home. A supply- and return-air strategy must be included to semi-condition the crawlspace.
In some areas of the country that do not have air conditioning, or if local requirements will not allow band joist insulation, it might be necessary to install a permanent dehumidification system in the crawlspace to maintain the 30%–50% humidity levels within the space.
Table 1 summarizes the conditions that will necessitate stopping all work on the crawlspace project. Once these problems have been solved, renovation work can resume.
Table 1. Critical Checklist
  When to Stop Work and Not Proceed
 If any mold or wood rot is observed during the initial inspection, then… A mold assessment professional will have to conduct an in-depth inspection and follow up with the proper remediation of the affected areas. No work can proceed until the space has been certified clean by the mold professional. Any rotten structural wood material must be removed and replaced.
 If there are questionable electrical practices or any exposed wiring that poses a safety threat, then…   A qualified electrician will have to conduct a thorough inspection of all wiring within the crawlspace and make necessary corrections to meet current code requirements.
 If the house has natural draft combustion appliances (furnace, water heater) located in the crawlspace, then… A qualified HVAC technician will have to conduct an analysis of the combustion makeup air strategy. The best practice would be to remove and replace all naturally vented appliances with direct-vent (two-pipe) models to ensure adequate combustion air and sealed exhausting when fuel-fired appliances are used.
 If recognizable signs of termite or other pest-related activity or damage are observed, then… A certified pest inspector will have to perform an inspection and apply treatment, if necessary, before renovation work can proceed.
 If standing water is observed anywhere on the crawlspace floor, then… The standing water will have to be removed, and the source of the water will have to be determined and eliminated.
 If measured radon levels exceed the EPA's acceptable levels, then… A radon mitigation professional will have to develop an appropriate strategy to be implemented.
 Preparation and Retrofit
The following information contains guidance on the ideal work sequencing when a crawlspace is retrofitted. It is up to the professional contractor to sequence the work so that moisture is not trapped within any of the building assemblies. Appendix A includes work plans and checklists to guide the work sequence, and Appendix B presents complete material specifications.
During the sealing process, the contractor must follow safe work practices to minimize any effects from sealants or adhesive fumes on workers’ health. It may be necessary to devise a means of temporary ventilation during the retrofit.
Exterior Moisture
Controlling bulk water on the exterior of the building is the first step to retrofitting a crawlspace. Ensure that all of the details to control bulk water that were identified during the evaluation process have been examined and corrected where necessary. For example, bulk water from the roof can be drained away from the foundation via downspouts that are connected to a storm sewer or collector crock pit, and bulk groundwater against the foundation can be drained away through a perimeter foundation drain system (see Figure 6).
Here are some additional specifics:
  • The moisture content of the wood in the crawlspace must remain below 17%. Moisture content greater than 17% is of concern and should be investigated.
  • Ideally, the grading around the perimeter of the building is at a 5% slope going away from the foundation (6 inches within the first 10 feet). If this is unachievable, evaluate the landscaping. Drainage swales or grade gutters might need to be installed at the perimeter of the foundation.
  • All lawn sprinkler flow must be directed away from the home.
  • All roof runoff must be directed away from the building a minimum of 10 feet or via an underground drain system.
Exterior Waterproofing and Drainage
Depending on site conditions, if there is high groundwater or recognizable bulk water flow against the foundation that cannot be remediated any other way, implementing a waterproofing or damp-proofing strategy might be necessary. Waterproofing or damp-proofing of all below-grade portions of the foundation and continuous perimeter drains might be required (at a minimum) to prevent subsurface groundwater from saturating the foundation system.
 Figure 6. Water management to keep bulk water away from the crawlspace
 Crawlspace Access
The general location and overall weather seal of the access door must be inspected. The access door (Figure 7) must be a minimum of 6 inches above the exterior grade to prevent runoff or snowmelt from entering. The door needs to be made of a non-corroding material, and the opening must be weatherstripped to prevent moisture and air from entering the space. Once all detailing is completed, a lock should be installed on the door.
If the access is too low and in contact with grade, it may be necessary to construct a well around the opening, with proper drainage at the base. If a well is not desirable, another method for providing access would be to install a new scuttle hole (Figure 8) through the floor system.
The 2015 IRC, Section R408.4, Access, states the following:
  • Access shall be provided to all under-floor spaces. Access openings through the floor shall be a minimum of 18 inches by 24 inches. Openings through a perimeter wall shall be not less than 16 inches by 24 inches. When any portion of the through-wall access is below grade, an areaway not less than 16 inches by 24 inches shall be provided. The bottom of the areaway shall be below the threshold of the access opening. Through-wall access openings shall not be located under a door to the residence. See Section M1305.1.4 for access requirements where mechanical equipment is located under floors.
 Figure 9 details the crawlspace exterior.
 Figure 7. Exterior access door
 Figure 8. Interior access door
 Figure 9. Crawlspace exterior details
 Contractor Prepares the Crawlspace Floor
Before working in the crawlspace, all the homeowner's possessions and all debris must be removed. The contractor must remove existing insulation and vapor barrier materials, and grade the crawlspace floor. Remove any rubble or sharp stones that could puncture the new vapor barrier (Figure 10). If possible, provide a 3% slope to the grade toward one or more low points, and install a drain or multiple drains. Fill any low spots, and smooth out the ground for an even application. Install a radon mitigation system, if necessary.
 Figure 10. Crawlspace floor
 Mechanical Systems
 Combustion Safety
The contractor must establish what type of space-conditioning equipment and water heater are currently in the crawlspace. If fuel-fired combustion appliances are located in the crawlspace, it is important to determine their venting and combustion air sources. These life-safety strategies are a critical first step in the overall renovation efforts. If natural draft-vented appliances that depend on combustion air from the open vents in the foundation are present, equipment upgrades and replacement or alterations to the makeup air methods will be necessary. The best strategy is to replace natural draft-vented appliances with sealed combustion, direct-vent furnaces or all-electric heat pumps. The direct-vent gas furnaces draw combustion air directly from outside through piping to the unit. All combustion byproducts are vented through sealed piping to the outdoors (see Figure 11), minimizing the possibility of any carbon monoxide spillage. Verify that an operational carbon monoxide detector is installed in the crawlspace. In addition, if the house has naturally ventilated combustion appliances, install carbon monoxide alarms (which comply with UL 2034) in close proximity to the combustion appliances and outside each separate sleeping area in the immediate vicinity of the bedrooms (UL 2008c). If natural draft-vented appliances exist and will not be upgraded, then identify an alternative combustion air source that meets or exceeds the International Mechanical Code (IMC) requirements for combustion air from indoors.
The 2006 International Mechanical Code requirements follow (p. 65). Each point is preceded by the section number within the code:
702.1 All air from indoors. Combustion and dilution air shall be permitted to be obtained entirely from the indoors in buildings that are not of unusually tight construction. In buildings of unusually tight construction, combustion air shall be obtained from the outdoors in accordance with Section 703, 705, 706 or 707.
 702.2 Air from the same room or space. The room or space containing fuel-burning appliances shall be in unconfined space as defined in Section 202.
702.3 Air from adjacent spaces. Where the volume of the room in which the fuel-burning appliances are located does not comply with Section 702.2, additional inside combustion and dilution air shall be obtained by opening the room to adjacent spaces so that the combined volume of all communicating spaces meets the volumetric requirement of Section 702.2. Openings connecting the spaces shall comply with Sections 702.3.1 and 702.3.2.
702.3.1 Number and location of openings. Two openings shall be provided, one within 1 foot of the ceiling of the room, and one within 1 foot of the floor.
702.3.2 Size of openings. The net free area of each opening, calculated in accordance with Section 708, shall be a minimum of 1 square inch per 1,000 BTU/h of input rating of the fuel-burning appliances drawing combustion and dilution air from the communicating spaces and shall not be less than 100 square inches.
 Figure 11. Direct vent furnace with combustion air intake and exhaust pipes directly to outdoors
In crawlspaces with combustion-type appliances, NFPA 720 requirements dictate installing a carbon monoxide alarm (NPFA 2012). Depressurization tests should be conducted if natural vented equipment (B-vent) is installed. These tests measure the pressure of the crawlspace in relation to the house and in relation to the outdoors. If the crawlspace is reading negative to the house or to the outdoors, it will be necessary to make adjustments to correct the imbalance. A negative reading indicates that the passive return might be too large or that the sealing on the return ductwork is unsatisfactory.
Ductwork
Visually inspect all ductwork located within the crawlspace, making sure the joints and connections are well-sealed. It is more important to pay attention to the sealing on the return-air ducts than the supply ducts because any supply leaks are adding conditioned air to the crawlspace, helping to condition the space. Sealing return leaks is more critical to minimize the potential for back-drafting of atmospherically vented equipment within the crawlspace. If the duct system is wrapped with insulation and the insulation is in good condition, a duct leakage test is recommended to determine the extent of system leakage. Depending on the amount of leakage, it may be necessary to remove the insulation to seal the ducts. In addition to air sealing, inspect the supports for all flexible ductwork. Strapping the flexible duct at 3-foot intervals will eliminate sagging and increase the air-delivery performance of the system (see Figure 12).
Figure 12. Seal and support duct system
Space Conditioning
Cost-effective ways to semi-condition the crawlspace and maintain a dry environment include making sure that the air handler furnishes the proper amount of conditioned supply air (Figure
13) and implementing a passive return strategy (Figure 14) to the living space. At a minimum, air should be delivered at a rate equal to 1 cfm for each 50 square feet of under-floor area, or 50 cfm total, whichever is greater. This strategy meets the requirements of the 2009
International Residential Code, Section R408.3 (IRC 2009b, p. 108); however, local codes may have different requirements.
Air-Conditioning Condensate Drainage
Make sure the condensate drain is routed, per local jurisdiction requirements, directly to a sealed drain point, such as a sealed sump crock lid, floor drain fitting, or the sanitary sewer system. In addition to the primary drain, and as a safety precaution if the primary drain fails, install an auxiliary drain pan with a separate drain beneath any cooling or evaporator coil to prevent any accidental spillage of condensate onto the crawlspace floor.
Dehumidifiers
Air-conditioning systems are not typically used in some mild- and cold-climate areas of the United States. In these conditions, it might be necessary to install a dehumidifier that is tied into a sealed drain point.
Figure 13. Supply air diffuser
Figure 14. Underside of passive vent in floor structure
Band Joist Insulation
Take extreme precautions when insulating band joist areas. The installer must assess the moisture potential of both the interior and exterior conditions where the mudsill, band joist and floor system all meet at the top of the crawlspace walls. If, in the installer’s judgment, the installation of insulation will not cause high moisture content in the wood and long-term rot, insulate this area. If there is any question about the drying potential at this area, the safest practice would be not to insulate and to allow free drying of the wood materials (Figure 15).
It is up to the contractor to determine the best order in which to seal the band joist and the vent opening sealing in relation to the vapor barrier installation.
If it has been determined that there is no risk of moisture at the band joist area, the following methods are recommended to air seal and insulate the band joist area:
  • Install close-fit and sealed-in-place 1½-inch unfaced rigid foam sheathing against the band joist (Figure 16).
  • Use 1½-inch direct-applied closed-cell spray foam.
Figure 15. Foam sealant at band joist insulation and penetrations
 Figure 16. Band joist insulation and air sealing
 Air Sealing
 Foundation Vent Sealing
Before undertaking any vent sealing, ensure that any necessary mechanical system makeup air strategies have been implemented and that makeup air from the foundation vents is not required.
Once the mechanical system air requirements have been verified, remove or patch over and seal all intentional, operable or fixed foundation vents to prevent outside air from being drawn into the crawlspace. If any vents are below grade, seal them from the outside with brick, block or concrete, and then insulate them from the inside. If the vent is to remain, verify that when the vent is closed, it will function as a pest-resistant barrier (or install a pest-resistant barrier, if needed). If the vent is being removed, create a durable pest- and weather-resistant barrier on the outside of any vent opening.
To seal the vent from the inside, follow these steps:
  • Measure and cut pieces of 2-inch extruded polystyrene rigid foam insulation to fit loosely over the vent area (see Figure 17).
  • Cut, install and seal the perimeter of the foam to the openings with expanding spray foam (see Figure 18 and Figure 19).
  • Consider the alternative of removing the vents and, if sizing is appropriate, replacing them with glass block that is mortared in place. This method allows some daylighting into the space.
Penetrations/Holes
Before installing the vapor barrier and insulating the walls, seal all gaps between the foundation wall and sill plate, sill plate and band joist, and band joist and subfloor. Seal penetrations through the crawlspace wall for water service, electrical service, plumbing fixtures, and ductwork using a non-shrinking cementitious grout or elastomeric caulk. If outdoor packaged-unit heating and cooling equipment is present, use solid blocking and sealants to seal gaps between the exterior wall opening and ductwork. Seal any wire or plumbing penetrations through the floor system above with caulk or expansive foam.
Figure 17. Measure existing foundation vent openings.
Figure 18. Cut rigid foam inserts to fit over the existing foundation vents.
Figure 19. Use spray foam to seal the edges of the foam inserts.
 Crawlspace Floor
 Poly Vapor Barrier
The floor of the crawlspace is a critical factor in eliminating moisture movement from the soil into the crawlspace environment. Improper installation of the vapor barrier will allow ground moisture to infiltrate the crawlspace and raise the relative humidity. Implementing a comprehensive vapor barrier strategy on the crawlspace floor is one of the most important tasks to carry out. For it to be successful, pay close attention to details.
Use the following best-practice steps as a guide to the proper application of a crawlspace vapor barrier:
  1. Clear all debris and sharp edges, and grade to a low-point drain (see Figure 20).
  2. Lap the vapor barrier up interior columns from a minimum of 4 inches to a maximum of 12 inches above the crawlspace floor (see Figure 21).
  3. Seal the connection between the vapor barrier and the columns with mesh tape and mastic (See Figure 21).
  4. Cover the entire crawlspace floor area with a minimum 10-mil or cross-laminated puncture-resistant 6-mil poly vapor barrier (see Figure 22). See Appendix B for material specifications.
  5. Lap the vapor barrier a minimum of 12 inches at sheet joints, and seal with tape. Secure with galvanized spikes and roofing tins to secure the poly to the ground. Seal penetrations with mastic (see Figure 22).
  6. Seal the vapor barrier to the interior surface of the foundation walls 4 inches below the top of the wall with mesh tape and mastic (see Figure 23 and Figure 24).
  7. Conduct a final inspection of the vapor barrier following all repair activities. Any tears or rips in the vapor barrier that might have occurred during other repairs must be sealed before the job is completed.
Under Section R408.3, Unvented Crawlspace, the 2009 IRC (IRC 2009b, p. 108) states the following:
  • Ventilation openings in under-floor spaces specified in Sections R408.1 and R408.2 shall not be required where exposed earth is covered with a continuous vapor retarder. Joints of the vapor retarder shall overlap by 6 inches and shall be sealed or taped. The edges of the vapor retarder shall extend at least 6 inches up the stem wall and shall be attached and sealed to the stem wall.
Figure 20. Clean and grade the crawlspace.
Figure 21. Lap the vapor barrier and seal the connection.
Figure 22. Apply poly vapor barrier and lap and seal the seams.
Figure 23. Use mesh tape to seal the vapor barrier to the interior surface of the foundation walls
 4 inches below the top of the wall.
Figure 24. Embed the mesh tape with mastic to complete the seal.
 Sump Pump Crock Pit and Floor Drain
Sump pump pits can contribute large amounts of moisture to the crawlspace if not detailed correctly. The lids to the crock pits are often missing, unattached, or sealed incorrectly. To eliminate this potential moisture source, make sure crock pits have well-sealed lids that fit tightly. If a sealable lid is not available, replace the entire unit. Once a sealed unit is installed, seal the vapor barrier on the crawlspace floor to the sump crock along the perimeter (Figure 25).
If a low-point floor drain has been installed, ensure that the perimeter of the drain is sealed to the vapor barrier (Figure 26).
Figure 25. Crock pit lid sealing
 Figure 26. Low-point floor drain sealing
 Wall Insulation
The 2009 International Energy Conservation Code prescriptive requirements for insulation levels for crawlspace walls (IECC 2009, p. 27, Table 402.1.1) are as follows:
  • Climate Zones 4 to 8 require either R-10 continuous insulated sheathing on the interior or exterior of the crawlspace, or R-13 cavity insulation at the interior of the crawlspace wall.
  • Climate Zone 3 requires R-5 continuous insulated sheathing or R-13 cavity insulation.
  • Climate Zones 1 and 2 do not require the use of insulation.
  • Although Climate Zones 1 and 2 do not require the use of insulation, crawlspaces in those regions are typically constructed above grade, and reasonable energy savings can occur if an insulation strategy is implemented. Consider insulation levels similar to those in Climate Zone 3 (see Figure 27).
 Figure 27. U.S. Climate Zone Map
In areas of the country that are prone to termite activity, the insulation will need to stop 3 inches short of the top of the foundation wall to allow for a pest control inspection strip. Consult with the local building inspector and pest control professional to determine the local requirements for the insect inspection strip at the top of the foundation wall.
Note that many rigid manufacturers apply a thin polyethylene film to both sides of the rigid panels to strengthen them and to make them impermeable to vapor. To provide some drying capability, source unfaced sheets, or remove the film before installation.
If the termite inspection strip is not needed, mechanically fasten 2-inch rigid foam sheathing to the crawlspace walls from the floor of the crawlspace to the bottom of the floor structure, or (as shown in Figure 28) to within 3 inches of the top of the foundation to allow for required inspections.
Then, add additional foam in the vent areas to even out the wall surface (Figure 29). Finally, foam seal the additional blocks in place (Figure 30).
Figure 28. Install rigid insulation to the crawlspace walls, allowing a 3-inch termite strip, if needed.
Figure 29. Vent area insulation
Figure 30. Vent area sealing
 Final Steps
Service Areas
Consider installing an additional protection layer (e.g., indoor/outdoor carpet runners, carpet protection mats) at the crawlspace entry and traffic areas to the mechanical equipment. This additional protection will help maintain the integrity of the vapor barrier. Additional convenience items to consider installing or having as a kit at the entrance are lighting, knee pads, dust masks, and a broom for sweeping cobwebs.
Water-Sensing Alarm
The installation of a water-leak alarm at a low spot or near the drain in the crawlspace is a good practice. These alarms alert the homeowners of potential pipe leaks or other unwanted water on the crawlspace floor that otherwise may go undetected for long periods of time.
 Vapor Barrier Inspection
As the last step in the crawlspace project, a final inspection of the vapor barrier should be conducted following all repair activities. Any tears or rips in the vapor barrier that may have occurred during other repairs must be sealed before the job can be deemed completed.
Additional Monitoring Equipment
As an option, consider installing a humidistat that allows the homeowner to track the performance of the crawlspace and to detect irregular moisture loading.
Figure 31.  Details of a complete interior crawlspace
Homeowner Education
Warning Sign
Post a warning sign at the entrance to the crawlspace about the system components and the importance of maintaining system integrity (Figure 32).
 Figure 32. Example of a warning sign posted at an access entryway
Trim Materials
Educate homeowners on the effects the drying process can have on finish materials within the living space. Wood floors and trim, as well as caulk joints, can shrink. Cupped floors might flatten as the wood dries out.
Glossary
  • combustion air:  The air provided to fuel-burning equipment, including air for fuel combustion, draft hood dilution, and ventilation of the equipment enclosure (IRC 2006, Section R202, p. 11).
  • condensate:  The liquid that separates from a gas due to a reduction in temperature; water that condenses from flue gases and water that condenses from air circulating through the cooling coil in air conditioning equipment (IRC 2006, Section 202, p.11).
  • confined space:  A room or space having a volume less than 50 feet3 per 1,000 BTU/h of the aggregate input rating of all fuel-burning appliances installed in that space (IRC 2006, Section 202, p. 11).
  • damp-proofing:  A water-resistant coating designed to shed water and resist soil moisture.
  • permeability (perm):  A measure of the diffusion of water vapor through a material at standard test conditions; there are dry-cup and wet-cup tests, and they sometimes yield different perm ratings.
  • semi-conditioning:  A method of providing intentional supply air to a space that will likely deviate by 5° F–10° F (or more) from the main thermostat set point.
  • waterproofing:  A continuous membrane covering that will resist standing water or water under hydrostatic pressure.
  • yard bubbler:  A drain pot installed over a dry well of rock that allows bulk water drainage to the soil through percolation; during extreme conditions, it allows an overflow to the surface through the bubble lid.
References
  • Advanced Energy (2005). Field Study Final Report: A Field Study Comparison of the Energy and Moisture Performance Characteristics of Ventilated Versus Sealed Crawl Spaces in the South. Raleigh, NC: Advanced Energy. Accessed November 1, 2012. http://www.advancedenergy.org/buildings/knowledge_library/crawl_spaces/pdfs/Field%20Study%20-%202005.pdf
  • Advanced Energy (2012). Closed Crawl Spaces: An Introduction to Design, Construction and Performance. Raleigh, NC: Advanced Energy. Accessed November 1, 2012: http://www.advancedenergy.org/buildings/knowledge_library/crawl_spaces/pdfs/Closed%20Crawl%20Spaces_An%20Introduction%20for%20the%20Southeast.pdf
  • ASTM C177. ASTM C177 – 10 Standard Test Method for Steady-State Heat Flux Measurements and Thermal Transmission Properties by Means of the Guarded Hot-Plate Apparatus. West Conshohocken, PA: ASTM International.
  • ASTM C509. ASTM C509 – 06 (2011) Standard Specification for Elastomeric Cellular Pre-Formed Gasket and Sealing Material. West Conshohocken, PA: ASTM International.
  • ASTM C518. ASTM C518 – 10 Standard Test Method for Steady-State Thermal Transmission Properties by Means of Heat Flow Meter Apparatus. West Conshohocken, PA: ASTM International.
  • ASTM C920. ASTM C920 – 11 Standard Specification for Elastomeric Joint Sealants. West Conshohocken, PA: ASTM International.
  • ASTM C1642. ASTM C1642 – 07 Standard Practice for Determining Air Leakage Rates of Aerosol Foam Sealants and Other Construction Joint Fill and Insulation Materials. West Conshohocken, PA: ASTM International.
  • ASTM D882. ASTM D882 – 12 Standard Test Method for Tensile Properties of Thin Plastic Sheeting. West Conshohocken, PA: ASTM International.
  • ASTM D3330. ASTM D3330/D3330M – 04(2010) Standard Test Method for Peel Adhesion of Pressure Sensitive Tape. West Conshohocken, PA: ASTM International.
  • ASTM E84. ASTM E-84 – 12b Standard Test Method for Surface Burning Characteristics of Building Materials. West Conshohocken, PA: ASTM International.
  • ASTM E283. ASTM E283 – 04 (2012) Standard Test Method for Determining Rate of Air Leakage Through Exterior Windows, Curtain Walls, and Doors Under Specified Pressure Differences Across the Specimen. West Conshohocken, PA: ASTM International.
  • ASTM E1745. ASTM E1745 – 11 Standard Specification for Plastic Water Vapor Retarders Used in Contact with Soil or Granular Fill under Concrete Slabs. West Conshohocken, PA: ASTM International.
  • ASTM E2178. ASTM E2178 – 11 Standard Test Method for Air Permeance of Building Materials. West Conshohocken, PA: ASTM International.
  • BPI (2010). -101 Home Energy Auditing Standard, Sections 7 and 3.2. Malta, NY: Building Performance Institute.
  • BSC (2004). Conditioned Crawl Space Construction, Performance and Code. Somerville, MA: Building Science Corporation. Accessed November 1, 2012: http://www.buildingscience.com/documents/reports/rr-0401-conditioned-crawlspace- construction-performance-and-codes
  • Federal Register (2005). Part IV Federal Trade Commission, 16 CFR Part 460 Labeling and Advertising of Home Insulation: Trade Regulations Rule; Final Rule. Federal Register, Vol. 70, No. 103, May 31, 2005. Washington, DC: U.S. Government Printing Office.
  • ICC-ES AC12. Acceptance Criteria for Foam Plastic Insulation. Whittier, CA: International Code Council Evaluation Service.
  • ICC-ES AC377. Acceptance Criteria for Spray-Applied Foam Plastic Insulation. Whittier, CA: International Code Council Evaluation Service.
  • IECC (2009). 2009 International Energy Conservation Code. Country Club Hills, IL: International Code Council, Inc.
  • IMC (2006). 2006 International Mechanical Code, Sections 702.1, 702.2, 702.3, 702.3.1, and 702.3.2. Country Club Hills, IL: International Code Council, Inc.
  • IRC (2006). 2006 International Residential Code, Section 202. Country Club Hills, IL: International Code Council, Inc., p. 11.
  • IRC (2009a). 2009 International Residential Code, Section R405.2.3. Country Club Hills, IL: International Code Council, Inc., p. 107.
  • IRC (2009b). 2009 International Residential Code, Section R408.3. Country Club Hills, IL: International Code Council, Inc.
  • IRC (2009c). 2009 International Residential Code, Section R408.4. Country Club Hills, IL: International Code Council, Inc.
  • NFPA (2009). NFPA 720: Standard for the Installation of Carbon Monoxide (CO) Detection and Warning Equipment. Quincy, MA: National Fire Protection Association.
  • UL 181 (2008a). UL 181A. Closure Systems for Use with Rigid Air Ducts. Camas, WA: UL. Accessed November 1, 2012: http://www.ul.com/global/eng/pages/solutions/standards/accessstandards/catalogofstandar ds/standard/?id=181A_3
  • UL 181 (2008b). UL 181B. Closure Systems for Use with Flexible Air Ducts and Air Connectors. Camas, WA: UL. Accessed November 1, 2012: http://www.ul.com/global/eng/pages/solutions/standards/accessstandards/catalogofstandar ds/standard/?id=181B_2
  • UL 2034 (2008c). Standard for Single and Multiple Station Carbon Monoxide Alarms. Camas, WA: UL. Accessed November 1, 2012: http://www.ul.com/global/eng/pages/solutions/standards/accessstandards/catalogofstandar ds/standard/?id=2034_3
 Appendix A:  Work Plans and Checklists
Stop-Work Items
The framing in the crawlspace has mold growing on the surface.
  • YES – A mold remediation professional will need to be hired to conduct a thorough inspection and remediation.
  • NO – Proceed.
There are exposed wiring and questionable electrical practices.
  • YES – The crawlspace will need to be inspected by a qualified electrician and the necessary repairs made.
  • NO – Proceed.
There are atmospherically (“B”) vented appliances located in the crawlspace.
  • YES – A qualified mechanical contractor will need to analyze the current equipment, and a new strategy of equipment replacement or alternative combustion air sources will need to be determined.
  • NO – Proceed.
There are signs of termite activity.
  • YES – A certified pest control contractor will need to conduct inspection and treatment.
  • NO – Proceed.
The crawlspace environment is saturated with moisture.
  • YES – Temporary dehumidifiers will need to be run to reduce humidity levels to between 30% to 50%.
  • NO – Proceed.
There is standing water on the floor of the crawlspace.
  • YES – The source will need to be identified and corrected and the standing water removed.
  • NO – Proceed.
There is a high radon level measured in the crawlspace.
  • YES – A radon mitigation strategy must be implemented within the process of closing the crawlspace.
  • NO – Proceed.
 Exterior Walk-Through
1.   Roof drainage strategy
  • Gutters at all roof eaves  _____
  • Downspout discharge distance  _____ feet
2.   Grading
  • Site grading slopes a minimum of 5% away from the foundation (6-inch fall over a 10-foot run).
  • YES ____    NO ____
3.   Lawn sprinklers
  • Activated and direction of flow away from the building _____
4.   Foundation waterproofing
  • Damp-proofing applied below grade _____
  • Footing drains discharge location _____
5.   Access door
  • Size of opening _____
  • Grade clearance to threshold  _____
  • Weather stripping installed YES _____ Location _____
Interior Walk-Through
Mechanical Systems
  1. Locate the mechanical systems within the crawlspace. If natural-draft exhaust appliances are installed in the crawlspace, combustion air zone (CAZ) testing has been conducted and compliance assured.
  2. Calculate necessary combustion air strategy to meet 2009 IRC 702.3.2:
    • 1 in.2 per 1,000 BTU/h and not less than 100 inches2
  1. Mechanical equipment
    • Furnace type, model, and manufacturer _____
    • Water heater type, model, and manufacturer _____
  1. Ductwork sealing
    • Supply duct joints and seams sealed with mastic _____
    • Return air ductwork sealed with mastic _____
  1. Space conditioning
    • Under floor area _____ feet2
    • Supply air volume set to local code requirements _____ cfm
    • Passive return or pathway to common area above floor _____
  1. Condensate drainage
    • Drain routing direct to drain point _____
  1. Carbon monoxide alarm
    • Working alarm installed in the CAZ per NFPA 720 _____
  1. Air pressure testing
    • CAZ testing performed _____
Air Sealing
1.   Foundation vent openings
  • Vents closed and rigid foam blocks installed _____
  • Foam blocks sealed with expanding foam _____
2. Penetrations
  • Sill plate to top of foundation wall sealed _____
  • Pipe penetrations sealed _____
  • Cracks or holes sealed, if applicable _____
3. Crawlspace floor
  • Vapor barrier type and millage _____
  • Vapor barrier installation
    • Floors: All seams sealed with construction tape _____
    • Floors: Penetrations sealed with construction tape _____
    • Floors: Sump pit crock lid sealed to vapor barrier _____
    • Floors: Floor drains sealed to vapor barrier _____
    • Walls: Top of barrier set in sealant _____
    • Columns: Vertical distance of barrier on column from floor _____ inches
 Thermal
1.   Wall insulation type _____
  • Pest inspection gap size at top of wall _____ inches
2.   Insulation permanently fixed to wall _____
  • Rigid insulation type meets local fire requirements _____
  • Band joist insulation size and type _____
  • Foam blocks in band area sealed to framing _____
Homeowner Awareness
1.   Warning sign installed within entryway _____
2.   Floor protection barrier
  • Additional protection barrier installed at entryway floor _____
  • Additional protection barrier installed at traffic areas _____
  • Humidistat (optional) _____
  • Water-sensing alarm _____
 Appendix B: Material Specifications
  • air barrier:  Any rigid or semi-rigid material that does not allow air to pass through it. Examples are gypsum board, plywood/oriented strand board, foam board, duct board (with a facing flame spread rating of 25 or less), sheet metal, or dimensional lumber.  Relevant test methods: ASTM E2178 and E283.
  • insulation:  Any material that significantly slows or retards the flow or transfer of heat. Building insulation types are classified according to form (e.g., loose-fill, batt, flexible, rigid, reflective, foamed-in-place) or material (e.g., mineral fiber, organic fiber, foam plastic).  Relevant test methods: ASTM C177, ASTM C518, CFR Title 16, Part 460.
  • rigid foam:  Rigid board material that provides thermal resistance. Examples are foam plastic, such as expanded polystyrene, extruded polystyrene, and polyisocyanurate.  Relevant test methods: ASTM C177, ASTM C518, ICC-ES AC12, CFR Title 16, Part 460.
  • sealant:  Any flexible product that, when applied to the joint of two or more materials, will adhere and permanently seal the joint to the passage of air. Examples are caulk, foam, and mastic.  Relevant test method: foam sealants—ASTM C1642.  Relevant test method: acrylic, silicone, and urethane caulk—ASTM C-920.  Required certification: water-based duct sealant—UL 181A-M, UL 181B-M.  Spray foam--relevant test Methods: ICC-ES AC377, ASTM E84, CFR Title 16, Part 460.  Tape (for ducts): required certification: UL-181. Tape (for air sealing): relevant test methods: ASTM D3330, ASTM D882.
  • vapor barrier.  Polyethylene sheeting that prohibits the passage of bulk water and vapor. Relevant test method: ASTM E1745.  Weatherstripping. relevant test method: ASTM C509.
InspectorSeek.com