Basic Electrical Inspection Guide
Standards of Practice
The International Standards of Practice for inspecting the electrical system is located at www.nachi.org/sop.
Free, Online Course
To learn more, take InterNACHI's free, online How to Perform Residential Electrical Inspections Course.
Weatherhead
Observation
Not minimum 13' height (NEC) above floor.
Observation
No bushing (phenolic insulator).
Observation
Inadequate drip loop.
Observation
Improper splices.
Illegal line-side tap (inside soffit).
Mast
Observation
Inadequate attachment to wall.
Observation
The mast is electrical metallic tubing (EMT) which is NOT an acceptable material. The mast should be of:
Intermediate metal conduit (IMC); or
Galvanized rigid conduit (GRC). Samples of each are attached to the wall.
Meter
Observation
The amperage rating of the 3/0 (225-amp) copper service entrance conductors exceeds the amperage rating of the electric meter socket enclosure (135 amps) as viewed on the meter label.
Observation
The bonding bushing conductor is in contact with phase lug.
Note:
Also attached to the wall is a section of polyvinyl chloride (PVC) conduit that is NOT acceptable as electrical mast material.
Electrical Panels-Panel #1 (Service Panel)
Observation
Description: GE 200-amp Main Breaker Panel with a 200-amp main disconnect (no other breakers).
Observation
Observation
Panel/components are not connected to a service grounding system (SGS) SGSs include:
Grounding electrode conductor (GEC);
Grounding electrode (examples: driven rod(s), concrete encased, grounding ring/plate, water pipe where acceptable).
Observation
Main lugs are double tapped to feed panel #2.
Observation
Panel/components are not connected to a service grounding system (SGS).
Distribution (sub-) Panel
Observation
The 200-amp service panel is inadequate for feeding the 200-amp.
Observation
Observation
A main bonding jumper connecting the neutral and grounding bus bars should be installed in the service panel only (point of first disconnect).
Observation
No conductors attached to bonding bushings.
Observation
Main feed conductor over-stripped (1" max. according to label).
Observation
A cable connector should be installed to protect the conductor insulation from abrasion.
CONDITIONS NOT DEFECTS:
Observation
The amperage rating of the 3/0 (225-amp) copper feeders exceeds the 200-amp maximum rating of the load center.
This is acceptable as long as the amperage rating of the main disconnect does not exceed the amperage rating of load center.
Observation
Multiple grounds under the same screw.
Observation
Vinyl insulation extends several inches into the panel.
Observation
Pig-tailed breaker.
GE 100-amp Main Breaker load center with no main disconnect. Backfed by 125-amp breaker. Circuit breakers are installed.
Observation
Unfilled holes.
Observation
Missing cable connector.
Observation
Deadfront cover attached with improper screws.
Sharp, course-thread screws can cut conductor insulation potentially causing a dangerous arc flash.
Observation
Deadfront cover missing filler plates (twistouts).
Observation
The amperage rating of the 125-amp backfeed breaker exceeds the 100-amp maximum amperage rating of both the #4 copper feeders and the load center.
The 125-amp backfeed breaker has no retaining device.
Observation
No bonding bushing.
Wherever feeders enter or leave a load center through concentric knockouts, a bonding bushing must be installed to ensure electrical continuity of the bonding/equipment grounding system. Bonding bushings should be connected to the neutral bus bar.
Observation
No insulated bushing is installed to protect feeders against abrasion where they enter the load center.
Observation
Observation
Multiple 20-amp breakers are connected to 14-gauge conductors. 20-amp breakers should be connected to 12-gauge conductors.
Observation
The GFCI breaker is connected to the grounding bus bar, not the neutral bus bar.
Observation
Multiple neutral conductors under the same screw in the neutral bus bar.
This is wrong because it complicates isolating the neutral for one of the circuits involved.
Observation
Pig-tailed neutrals.
Again, this is wrong because it complicates isolating the neutral for one of the circuits involved.
Observation
Neutral conductor.
Observation
In order to complete their insertion into the 125-amp breaker (lower right corner) the #1 (150-amp) copper conductors had strands cut away.
Cutting strands reduces the amperage rating of a conductor. 37. Unfilled Knockout.
Observation
Unfilled Knockout.
Observation
Grounding conductor on the neutral bus bar.
First Detached Structure Electrical Panel
Square D 125-amp load center, backfed by 125-amp breaker.
Grounding conductors of different gauges under the same screw. The 125-amp backfeed breaker has no retaining device. Neutral and grounding bus bars are not isolated from each other.
Second Detached Structure Electrical Panel
Observation