Nick Gromicko and his staff have constructed a problem panel as a mini-inspection tutorial. This pictorial training article is a must for inspectors who want to be better prepared to spot problems with residential electrical service panels, including service size, wiring, connections, and issues with the panel's labeling and exterior.
This photo shows a meter socket, load center, and auxiliary panel.
The photos above show undersized service conductors and a 200-amp service disconnect with #2 aluminum conductors. They should be 4-0.
A reducing washer has been used on concentral knockouts of an ungrounded meter base, which does not meet service bonding requirements.
A non-wet location fitting has been used for entering the panel above an energized bus.
A horn bypass meter has been installed instead of a lever bypass. For new
construction, all PUDs and MUDs have adopted the new lever bypass meter.
The lever bypass meters provide meter maids with a safe-to-use lever
so that they don't need to install a jumper or shut off the electricity
to the house.
Not all strands are under the set screw of the lug.
This shows a modified or damaged bus, which is often found when someone tries to install a breaker that doesn't belong in the panel.
This photo shows breakers that are not listed for the panel, as well as multiple brands of breakers.
Depicted above is a double-lugged or double-tapped breaker.
This is a damaged breaker.
This is an over-fused conductor: a 20-amp breaker protecting a 14-gauge conductor.
The neutral and ground bus bar are not bonded to the panel, as indicated by:
- no green screw;
- no copper bond strap; and
- no #4 conductor bonded to the panel.
There is also debris in the bottom of the panel.
This conductor runs over an energized bus.
This is a loose conductor at the breaker.
Multi-wire branch circuit issues shown above are indicated by:
- a mismatched tandem breaker on a single phase of the bus; and
- multi-wire branch circuit wires that are not grouped or zip-tied.
This phase conductor is not identified. It should be taped, typically using red tape (anything but white or green). It is also a 10-2 (two-conductor) cable used for a dryer circuit requiring four conductors.
This is a nicked (exposed) conductor.
This shows three neutral conductors on one lug. Only one neutral conductor per lug is allowed.
Three cables are entering this panel through one strain-relief fitting.